Updates:

Click here to visit our store! https://www.auberins.com

1/16 DIN Humidity Controller (Relay Output)

Started by Stumpy, May 14, 2012, 10:35:48 PM

Previous topic - Next topic

Stumpy

I have one of these and hope to run a  humidifier and a dehumidifier. If I want a R/H of 75%. What would be the settings on the controller be?

colnny

#1
Connect the humidifier with its power to the output of the controller (terminals 7 and 8, assume the current is less than 10A). Connect the dehumidifier with its power to the AL1 relay (if it draws more than 3A, you need a contactor). Set the SV to 75. Set ALM1 to 76.

Then, the humidifier will be on when R/H is lower than 74.7%, will be off when it's higher than 75.3%. The dehumidifier will be on when R/H is higher than 76.3%, will be off when it's lower than 75.7%.