240 volt led with ssvr piolet light

Started by Hardtail, November 25, 2018, 02:12:52 PM

Previous topic - Next topic

Hardtail

Was wondering if someone had a schematic
For how to wire a 240 volt led poilet light to a
sssvr to Indicate status of energized or not

Kkane

Wiring is simple. You need to wire the indicator in parallel to the output of the SSVR. So this indicator is wired in parallel to your load/heater.

But the issue is, SSVR is not an on/off switching device. When output is 0%, it is OFF. When output is not 0%, it is ON. When the output increases, the average output voltage will increase as well. So if you want to use a indicator to show the output status, you need to use a 240V dimmable LED indicator or 240V incandescent light bulb. So you can tell whether this indicator is fully ON or not.

Here is a discussion for the output comparisons between SSVR, PID and DSPR.

https://www.auberins.com/images/Manual/EZboil_talkv1.1.pdf